What is the maximum 2 pole breaker size allowed for each Q Cable (12AWG) PV AC branch circuit?

Explanation:
The limit is set by the conductor’s ampacity and the listing of the Q Cable. A 12 AWG copper PV AC branch circuit is protected up to 20 amperes, so the maximum 2-pole breaker you can use for each Q Cable is 20 A. This protects the insulation and prevents overheating of the cable while still allowing typical inverter output on that branch. An 80 A breaker would exceed what the 12 AWG cable is rated to carry, and a 15 A breaker underutilizes the conductor and isn’t the listed maximum. The count of microinverters on the circuit doesn’t change this limit—the cable’s rating does.

The limit is set by the conductor’s ampacity and the listing of the Q Cable. A 12 AWG copper PV AC branch circuit is protected up to 20 amperes, so the maximum 2-pole breaker you can use for each Q Cable is 20 A. This protects the insulation and prevents overheating of the cable while still allowing typical inverter output on that branch. An 80 A breaker would exceed what the 12 AWG cable is rated to carry, and a 15 A breaker underutilizes the conductor and isn’t the listed maximum. The count of microinverters on the circuit doesn’t change this limit—the cable’s rating does.